Except above suspended ceilings.

In new work, I usually mount a J-box on the NM that I poked out of the wall during rough-in, and run MC from there.

In existing work, I sometimes drop NM to the outlet as above, and sometimes drop the MC all the way to the outlet.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
It is covered by 334.10(3), if the building code required that type of construction.

The use of NM is not based on the actual construction of the building, but based on what construction the building code would permit. If you have a Type I or II building, you can still use NM if the building code would have permitted a different Type of building construction.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
It is covered by 334.10(3), if the building code required that type of construction.

The use of NM is not based on the actual construction of the building, but based on what construction the building code would permit. If you have a Type I or II building, you can still use NM if the building code would have permitted a different Type of building construction.


I did not know that. Thank you

I always read the "permitted to be" to be how it was on the permit. haha
 

James L

Senior Member
Location
Kansas Cty, Mo, USA
Occupation
Electrician
Except above suspended ceilings.
"Within" suspended ceilings. It's technical, because "within" the suspended ceiling means between the grid and the eyelets where the wires are fastened.

I wired a whole business park in NM, not one stitch of MC. I ran above trusses, which are "above" the suspended ceilings, not "within" the ceilings.

Then I dropped straight down to inside the walls, and that got technical too.

The walls are not "within" the ceiling, either. The perimeter of the ceiling is where the wall angle sits against the wall. There's 4-3/4" of space between two ceilings if there's a sheetrocked wall between them.
 

david

Senior Member
Location
Pennsylvania
"Within" suspended ceilings. It's technical, because "within" the suspended ceiling means between the grid and the eyelets where the wires are fastened.

I wired a whole business park in NM, not one stitch of MC. I ran above trusses, which are "above" the suspended ceilings, not "within" the ceilings.

Then I dropped straight down to inside the walls, and that got technical too.

The walls are not "within" the ceiling, either. The perimeter of the ceiling is where the wall angle sits against the wall. There's 4-3/4" of space between two ceilings if there's a sheetrocked wall between them.
How is what your describing not in an un-cancelled area. Cancelled (not exposed) the area out-side of the cancelled space 15 min. fire protection. Not in an accessible area to protect against physical damage.

Cancelled in walls floors or ceilings, ceiling joist, floor joist and studs are different than roof rafters.

The area must provide concealment of the NM cables
 
"Within" suspended ceilings. It's technical, because "within" the suspended ceiling means between the grid and the eyelets where the wires are fastened.

I wired a whole business park in NM, not one stitch of MC. I ran above trusses, which are "above" the suspended ceilings, not "within" the ceilings.

Then I dropped straight down to inside the walls, and that got technical too.

The walls are not "within" the ceiling, either. The perimeter of the ceiling is where the wall angle sits against the wall. There's 4-3/4" of space between two ceilings if there's a sheetrocked wall between them.
Interesting take. Never considered that, but not sure I am convinced. Actually the NEC does not use the word "within" it uses "in". Plus you have 334.10(3) which would require being "concealed" with a 15 minute rating.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
"Within" suspended ceilings. It's technical, because "within" the suspended ceiling means between the grid and the eyelets where the wires are fastened.
So, your take is that the space tops out where the support attachments are?

What would you say if a new ceiling grid was hung from an old ceiling grid?
 

James L

Senior Member
Location
Kansas Cty, Mo, USA
Occupation
Electrician
Interesting take. Never considered that, but not sure I am convinced. Actually the NEC does not use the word "within" it uses "in". Plus you have 334.10(3) which would require being "concealed" with a 15 minute rating.
It specifically says "within"
 

Attachments

  • 20210321_155300.jpg
    20210321_155300.jpg
    128.6 KB · Views: 6

david

Senior Member
Location
Pennsylvania
keep in mind the 15 min rating is to keep a potential fire source concealed from unconcealed areas to slow down the fire spread, Many suspended ceilings can be rated for 15 min. But now you have to deal with access to the cables for potential physical damage to NM cable that is why suspended ceilings have removable panels to allow access to what's exposed above them
 

James L

Senior Member
Location
Kansas Cty, Mo, USA
Occupation
Electrician
keep in mind the 15 min rating is to keep a potential fire source concealed from unconcealed areas to slow down the fire spread, Many suspended ceilings can be rated for 15 min. But now you have to deal with access to the cables for potential physical damage to NM cable that is why suspended ceilings have removable panels to allow access to what's exposed above them
Most grid ceilings are at least 1hr rated.
I get the physical damage part. But if there are trusses above, it's next to impossible to find tiles up there. Guys slide them onto the next tile or take them out.
 