I have type IIIB construction one story commercial office that is wired nm cable. Code does not allow nm am i correct?
I have type IIIB construction one story commercial office that is wired nm cable. Code does not allow nm am i correct?
It must be concealed 334.15 would not apply NMC cable cannot not be exposed in your application
It is covered by 334.10(3), if the building code required that type of construction.
The use of NM is not based on the actual construction of the building, but based on what construction the building code would permit. If you have a Type I or II building, you can still use NM if the building code would have permitted a different Type of building construction.
"Within" suspended ceilings. It's technical, because "within" the suspended ceiling means between the grid and the eyelets where the wires are fastened.Except above suspended ceilings.
How is what your describing not in an un-cancelled area. Cancelled (not exposed) the area out-side of the cancelled space 15 min. fire protection. Not in an accessible area to protect against physical damage."Within" suspended ceilings. It's technical, because "within" the suspended ceiling means between the grid and the eyelets where the wires are fastened.
I wired a whole business park in NM, not one stitch of MC. I ran above trusses, which are "above" the suspended ceilings, not "within" the ceilings.
Then I dropped straight down to inside the walls, and that got technical too.
The walls are not "within" the ceiling, either. The perimeter of the ceiling is where the wall angle sits against the wall. There's 4-3/4" of space between two ceilings if there's a sheetrocked wall between them.
Interesting take. Never considered that, but not sure I am convinced. Actually the NEC does not use the word "within" it uses "in". Plus you have 334.10(3) which would require being "concealed" with a 15 minute rating."Within" suspended ceilings. It's technical, because "within" the suspended ceiling means between the grid and the eyelets where the wires are fastened.
I wired a whole business park in NM, not one stitch of MC. I ran above trusses, which are "above" the suspended ceilings, not "within" the ceilings.
Then I dropped straight down to inside the walls, and that got technical too.
The walls are not "within" the ceiling, either. The perimeter of the ceiling is where the wall angle sits against the wall. There's 4-3/4" of space between two ceilings if there's a sheetrocked wall between them.
So, your take is that the space tops out where the support attachments are?"Within" suspended ceilings. It's technical, because "within" the suspended ceiling means between the grid and the eyelets where the wires are fastened.
It specifically says "within"Interesting take. Never considered that, but not sure I am convinced. Actually the NEC does not use the word "within" it uses "in". Plus you have 334.10(3) which would require being "concealed" with a 15 minute rating.
above a grid ceiling is another grid ceiling?So, your take is that the space tops out where the support attachments are?
What would you say if a new ceiling grid was hung from an old ceiling grid?
I think there's an intent there, that NM be concealed and not exposed. Because it specifically mentions ceilings, it clearly does not have grid ceilings in view334.10(3) which would require being "concealed" with a 15 minute rating.
Most grid ceilings are at least 1hr rated.keep in mind the 15 min rating is to keep a potential fire source concealed from unconcealed areas to slow down the fire spread, Many suspended ceilings can be rated for 15 min. But now you have to deal with access to the cables for potential physical damage to NM cable that is why suspended ceilings have removable panels to allow access to what's exposed above them
Interesting, they changed it in 2017 or 2020. 2014 says "in"It specifically says "within"