Z Zapper1247 New User Location Florida Occupation Engineer Feb 7, 2020 #1 I need help please, can the motor disconnect for a commercial overhead door operator be located next to the operator (upwards of 18-20’)?
I need help please, can the motor disconnect for a commercial overhead door operator be located next to the operator (upwards of 18-20’)?
tom baker First Chief Moderator & NEC Expert Staff member Location Bremerton, Washington Occupation Master Electrician Feb 9, 2020 #2 One disconnect must be readily accessible and the other accessible. The disconnect that is by the opener must be within sight, this would be the opener up in the ceiling. The readily available is typically at the power source panel.
One disconnect must be readily accessible and the other accessible. The disconnect that is by the opener must be within sight, this would be the opener up in the ceiling. The readily available is typically at the power source panel.