I'm sure I'll get a few different responses for this, and might start an argument or two, but, in commercial construction, in a panel schedule or panel calculation, how do you account for plugmold strips? I've never run into a situation where I needed to know before now, and I'm not sure how to allow for it. I'm pretty sure receptacles are 180W per, and no I can't cite the code reference, but on this plugmold, there's 10 single receptacles. Does anyone know?
 
Commercial Plugmold

Commercial Plugmold

Article 220.14 (H) covers load calculations for multioutlet assemblies. When the outlets are unlikely to be used simultaneously its 180va for each 5 foot, or 180 va for each 1 foot when the receptacles are likely to be used simultaneously
 