I agree with Ethan. I don't fully understand the physics, so I can't explain the situation completely. The basic issue is that the behavior of the upstream "current-limiting fuse" (CLF) will be influenced by the behavior of any downstream device (breaker or fuse) that will itself react to high currents by attempting to terminate the event. So if the thing you are trying to protect at 10KA is, for example, a controller for an elevator or an air conditioning system, then that controller's internal fuses will change the way the CLF will function during a fault. The result is that the CLF may wind up passing more than the desired limit of 10KA down to the controller.
A solution that I have used in the recent past is to insert a series reactor upstream of the controller you are trying to protect.