Turboburke
Member
Hi Mike ? hope you are having a great weekend.
OKAY ? I am having a slightly difficult time determining whether or not I am required to utilize a FUSED service disconnect in my installation.
I am starting with what appears to be a 300 amp 120/208 service ( The xfmr 3 pack on the pole is marked ?100 KW? ? if I did my math right that should supply 278 amps at 100% load: 100,000 divided by 208= 480.77 divided by 1.73 = 277.8 amps ). The aerial hits the building with what appears to be something in the neighborhood of 3 aut wire ( free air), passes thru a CT set, and then immediately bugs into what looks like 350 or 500 MCM. These MCM conductors enter the weatherhead and travel down a 4? rigid, thru a longmouth LB and through the wall of the building. INSIDE, the 4? nipple exits the block and travels about a foot and enters a 12? X 12? by 6 foot long trough. Mounted atop this trough is FOUR 200 amp panels; TWO of them are 3 phase and the other TWO are single phase. The 3 AUT copper conductors from each of these main breakers travel down into the trough, where the whole shebang is supertapped together (The incoming MCM?s and all FOUR panel mains). Now I understand that each individual panel?s main supply is protected by it?s own panel main breaker. If a panel overloads, it?s main trips and the supply is protected.
WHAT I want to do is install a 400 amp disconnect on the side of the trough opposite where the MCM? come in, remove the MCM?s from the supertaps, and extend the unprotected MCM?s from the weatherhead all the way into the line side of my disconnect. Then, I want to run parallel 3 AUT?s from the load side of my disconnect into the UTILITY side of a 400 amp XFR switch. Finally, I want to run another set of parallel 3 AUTs from the load side of the XFR switch back to feed the supertaps.
DO I need a FUSED 400 amp disconnect, or not? I just can?t seem to determine this one piece of my puzzle. Thanks so very much for your help!
OKAY ? I am having a slightly difficult time determining whether or not I am required to utilize a FUSED service disconnect in my installation.
I am starting with what appears to be a 300 amp 120/208 service ( The xfmr 3 pack on the pole is marked ?100 KW? ? if I did my math right that should supply 278 amps at 100% load: 100,000 divided by 208= 480.77 divided by 1.73 = 277.8 amps ). The aerial hits the building with what appears to be something in the neighborhood of 3 aut wire ( free air), passes thru a CT set, and then immediately bugs into what looks like 350 or 500 MCM. These MCM conductors enter the weatherhead and travel down a 4? rigid, thru a longmouth LB and through the wall of the building. INSIDE, the 4? nipple exits the block and travels about a foot and enters a 12? X 12? by 6 foot long trough. Mounted atop this trough is FOUR 200 amp panels; TWO of them are 3 phase and the other TWO are single phase. The 3 AUT copper conductors from each of these main breakers travel down into the trough, where the whole shebang is supertapped together (The incoming MCM?s and all FOUR panel mains). Now I understand that each individual panel?s main supply is protected by it?s own panel main breaker. If a panel overloads, it?s main trips and the supply is protected.
WHAT I want to do is install a 400 amp disconnect on the side of the trough opposite where the MCM? come in, remove the MCM?s from the supertaps, and extend the unprotected MCM?s from the weatherhead all the way into the line side of my disconnect. Then, I want to run parallel 3 AUT?s from the load side of my disconnect into the UTILITY side of a 400 amp XFR switch. Finally, I want to run another set of parallel 3 AUTs from the load side of the XFR switch back to feed the supertaps.
DO I need a FUSED 400 amp disconnect, or not? I just can?t seem to determine this one piece of my puzzle. Thanks so very much for your help!