You agree that it is your design minimum? NEC allows us to run 14 AWG/15 amp circuits for most general use lighting and receptacles. Most of the 20 amp minimum requirements are in dwellings for the small appliance circuits, bathroom circuits, the laundry circuit, now in the garage.I agree with 12 AWG min for receptacle circuits but I see no need for 20 A Tslot devices
Voltage drop is dependent on the load as well. If you only have a ~3 amp fixed load, you can run quite a long circuit and 14 AWG is still not giving much VD issues, especially if supply is 480 volts.20 amp minimum circuit breaker size is the common specified minimun, however be careful when wiring to small motors, if a 15 amp breaker is the correct size for the motor load, the code does not allow the circuit breaker to be upsized to 20 amps.
#12 awg wire is the common minimum wire size. If you do have 15 amp circuits I would be very careful using #14awg wire. Voltage drop can be a problem with # 14 wire.
I don't have a problem with using 15 amp circuit breakers if this is the right size breaker for the application, but I never use #14 wire because of voltage drop.
Voltage drop is dependent on the load as well. If you only have a ~3 amp fixed load, you can run quite a long circuit and 14 AWG is still not giving much VD issues, especially if supply is 480 volts.
You do realize that, unless you're talking about percentage, the voltage is not relevant to voltage drop for a given current, don't you? For a given wattage, yes.Voltage drop is dependent on the load as well. If you only have a ~3 amp fixed load, you can run quite a long circuit and 14 AWG is still not giving much VD issues, especially if supply is 480 volts.
We never use watts in VD calculations, always current.You do realize that, unless you're talking about percentage, the voltage is not relevant to voltage drop for a given current, don't you? For a given wattage, yes.