Is this for a dwelling or commercial kitchen?Can a comerical cooktop or griddle use a demand factor from table 220.55 or does table 220.56 only apply? I'm looking at a griddle has a nameplate of 21.5 kw at 89 amps. The voltage is 240 volts.
It's actually a barn that will be used for wedding venues.Is this for a dwelling or commercial kitchen?
Then it's not a dwelling and can't use 220.55It's actually a barn that will be used for wedding venues.
Me too. It had #2 SER AL installed on it.I'm surprised it's not 3 phase.