Engineer used NEC 2017 Article 220.54 demand factors in commericial laundromat sub panel demand load calculation. Sub panel is 208/120V three lhase.
NEC 2017 Article 220.54 is for dwelling units. I don’t see anywhere else it can be used for commericial laundromat.
Am I correct or incorrect NEC 2017 Article 220.54 doesn’t apply to commericial laundromat? If it doesn’t apply then which section in NEC 2017 Article 220 applies to commericial laundromat?
NEC 2017 Article 220.54 is for dwelling units. I don’t see anywhere else it can be used for commericial laundromat.
Am I correct or incorrect NEC 2017 Article 220.54 doesn’t apply to commericial laundromat? If it doesn’t apply then which section in NEC 2017 Article 220 applies to commericial laundromat?