I'm just wondering about these two requirements in the NEC and if they are a requirement for even bonding the GC at a detach garage? and if not what were they put into the code for?
250.94 Bonding for Other Systems.
An accessible means external to enclosures for connecting intersystem bonding and grounding conductors shall be provided at the service equipment and at the disconnecting means for any additional buildings or structures by at least one of the following means:
250.50 Grounding Electrode System.
If available on the premises at each building or structure served , each item in 250.52(A)(1) through (A)(6) shall be bonded together to form the grounding electrode system. Where none of these electrodes are available, one or more of the electrodes specified in 250.52(A)(4) through (A)(7) shall be installed and used.
250.94 Bonding for Other Systems.
An accessible means external to enclosures for connecting intersystem bonding and grounding conductors shall be provided at the service equipment and at the disconnecting means for any additional buildings or structures by at least one of the following means:
250.50 Grounding Electrode System.
If available on the premises at each building or structure served , each item in 250.52(A)(1) through (A)(6) shall be bonded together to form the grounding electrode system. Where none of these electrodes are available, one or more of the electrodes specified in 250.52(A)(4) through (A)(7) shall be installed and used.