I commonly find warehouse spaces with switchgear in an electrical room have a copper bus bar with the GEC, bldg steel, and other bonding wires landed on that bus bar (outside the service enclosure on the wall). Im installing a 2500A service in a similar warehouse setup and wanted to do a common grounding electrode as well. I have rebar which serves as the main bldg GEC, building steel bond, gas bond, water bond, riser sprinkler bond, and xfmr GEC in same room per articles I mentioned does anyone see any potential issues of such an installation granted that the GEC taps are connected to the bus bar with listed methods for grounding and bonding? Another article that I believe supports this installation is 250.64 F. Thank you