Recently I did a walk through in a large office building that had a 500 kcmil common grounding electrode riser that ran from floor to floor through the electric closets. This conductor terminated at a grounding bus in each closet for the connection of any GEC's from each separately derived system within that closet.
The contractor installed a 2" EMT sleeve about 24" long to protect the conductor as it passed through the floor. My question is at what point or at what length does this sleeve need to be bonded to the GEC? GEC's in ferrous metallic conduits require that the conduit be bonded to it at both ends. Would a 24" sleeve require this? Opinions please.
The contractor installed a 2" EMT sleeve about 24" long to protect the conductor as it passed through the floor. My question is at what point or at what length does this sleeve need to be bonded to the GEC? GEC's in ferrous metallic conduits require that the conduit be bonded to it at both ends. Would a 24" sleeve require this? Opinions please.