common neutral on 20/30A ckts

Status
Not open for further replies.

rob1955

Member
I had one of my electricians ask me this question today, and I couldn't answer him. Is it a code violation for a 20 amp and a 30 amp branch circuit to share a common neutral? I guess the kicker is the common "tied" breaker, which I've always seen the poles being the same amperage. In this case the two tied breakers would need to be different amperages.
 
rob1955 said:
Is it a code violation for a 20 amp and a 30 amp branch circuit to share a common neutral?

No.

rob1955 said:
I guess the kicker is the common "tied" breaker,

The breakers may not have to be tied or even beside each other depending on what is being supplied. (This will change in 2008)

480sparky said:
What kind of load would need 20amps on one side and 30amps on the other?

In my case a small appliance branch circuit and a 120 volt 30 amp point of use hot water heater.

It was an office remodel and I ended up re-using a 6/3 MC cable that had fed a range.
 
Brain fart on my part. I was trying to envision a 120/240v load, not a MWBC.

In that case, yes, you can share the neutie.
 
Let's just add that the shared conductor must be sized for the largest breaker.

iwire said:
In my case a small appliance branch circuit and a 120 volt 30 amp point of use hot water heater.

It was an office remodel and I ended up re-using a 6/3 MC cable that had fed a range.
Bob certainly complied on that one! :)
 
I appreciate the input. And yes, this is two different circuits sharing the same neutral, and the neutral is sized for #10. I looked and looked through the code book, and couldn't find anywhere that said this couldn't be done. Again, thanks!
 