common neutral

Status
Not open for further replies.

sevlander

Member
Location
new jersey
Does the NEC allow common neutrals for multi-wire circuits feeding HID and/ or Fluoresent lighting? I was under the impression it was no longer allowed on HID circuits, but find it nowhere? Am I misinformed or has this changed with any codes. If it is not, what article please? Thanks, Scott
 
MWBC's are allowed for HID and Flourescent lighting circuits and in fact, they are quite common for this.

Roger
 
sevlander said:
Does the NEC allow common neutrals for multi-wire circuits feeding HID and/ or Fluoresent lighting? I was under the impression it was no longer allowed on HID circuits, but find it nowhere? Am I misinformed or has this changed with any codes. If it is not, what article please? Thanks, Scott

2008 NEC. MWC's are permitted for fluorescents as prescribed in 410.130(G). See 410.130(F) for HID, but I see nothing that prohibits MWC's for HID. :)
 