I am much too frequently amazed how little electricians in the field understand about grounding a transformer.
I often find grounds from Building steel , the water main and other perfectly good grounding sources on lugs
bolted to the case of the transformer without a single connection to XO. I found a building that had a live ceiling grid.
(the steel studs had to be live also)
The transformer has no grounding connection to XO so when a sheet rocker or ceiling grid person drilled a screw through the MC cable and hit a phase wire everything connected to the steel was live. This was not a new building. It was likely this way for many years. (Cheshire Connecticut)
I recently found another where a transformer installed at a college to boost 208V to 280/277V for the long runs to light poles down a long driveway and parking lot.
No ground to the common! What could possibly go wrong ????? We repaired the 15 year old problem...
EdF
Inspectors should consider asking to see transformer connections.
It takes time but would be worthwhile
Frustrated!!!
I often find grounds from Building steel , the water main and other perfectly good grounding sources on lugs
bolted to the case of the transformer without a single connection to XO. I found a building that had a live ceiling grid.
(the steel studs had to be live also)
The transformer has no grounding connection to XO so when a sheet rocker or ceiling grid person drilled a screw through the MC cable and hit a phase wire everything connected to the steel was live. This was not a new building. It was likely this way for many years. (Cheshire Connecticut)
I recently found another where a transformer installed at a college to boost 208V to 280/277V for the long runs to light poles down a long driveway and parking lot.
No ground to the common! What could possibly go wrong ????? We repaired the 15 year old problem...
EdF
Inspectors should consider asking to see transformer connections.