Question: do cable trays containing only communication cables have to be bonded. I believe yes but dont think it can be enforced.
Code book: 2020 but 2023 would work too
Logic: 90.3= article 800 is exempt from article 250 or 392 requirements unless specifically called out in article 800
800.110 A1= raceways have to be installed per their article. This would make cable tray something that needs bonded under articles 392 and 250, except cable tray isn’t a raceway. Therefore it cant be enforced under this.
392.60= non-power cable tray is mentioned, but according to 90.3 and the informationsl note, this is class 2 or 3 type examples.
800.110 D= cable tray can be used for communication cabling, doesnt mention bonding.
Thoughts?