Re: Communication closet grounding
OBO, this is difficult to explain on the forum.
Is your equipment DC powered or AC powered??
If it is AC powered you use the techniques outline by NEC article 250. The grounds serve a one main purpose and that is to clear a fault and operate the OCPD.
If it is DC powered (by a battery/rectifier plant) the techniques are some what different, but similar. The equipment frame grounds only purpose is to clear faults as AC powered equipment. The main difference is the EGC is not typically run with the battery conductors and are larger to overcome the lower voltages and long distances encountered.
There are sometimes other ground conductors used by the equipment. One is what is called a discharge ground. The discharge ground is used terminate surge protectors, cable protectors, and cable shields. Normally these conductors do nothing until an inside/outside plant cable is struck by lightning or comes in contact with high voltage. At that point the surge arrestors operate and discharge the energy to ground via its dedicated conductor. By using a dedicated conductor any faults are routed around any sensitive equipment.
Another type of ground is what is called a logic or signal ground. This ground is used to reference the various signal receivers used in telecom equipment. Again this is dedicated ground used for only one dedicated purpose. This is what is sometimes known as a low noise ground, but that is really a myth because any length of wire exhibits a high impedance at the higher frequency?s and acts like an antenna.
The trick is originating any type of ground (except GEC and discharge) from the power source be it whatever like a DC power plant, isolation/step-down transformer, or AC service entrance. They originate from the main bonding point to the grounded circuit conductor if used.
What is important is that all the grounds are bonded together. Typically in a phone office this point is call the Office Principle Ground Point Bus (OPGPB). The OPGPB is a bus bar where all the ground electrodes are terminated too in a radial fashion to form a low impedance connection to earth at low frequencies (not possible to have low impedance connections at high frequencies using cable). Then from the OPGPB all the grounds are fed out radially via dedicated conductors to the various systems like AC service entrance, DC plants, discharge devices, SDS, signal/logic, raised floor grids, etc.