J jjavier Member Location Maine Apr 21, 2017 #1 In the communication pull box with one conduit 2"pvc, is it the same rule 6*2 = 12" minimum dimension than electric boxes?
In the communication pull box with one conduit 2"pvc, is it the same rule 6*2 = 12" minimum dimension than electric boxes?
C Carultch Senior Member Location Massachusetts Apr 21, 2017 #2 jjavier said: In the communication pull box with one conduit 2"pvc, is it the same rule 6*2 = 12" minimum dimension than electric boxes? Click to expand... That rule is specific to #4 and larger conductors. I don't think you'll have a communication cable that large. In any case, you still do need to plan for proper bend radius.
jjavier said: In the communication pull box with one conduit 2"pvc, is it the same rule 6*2 = 12" minimum dimension than electric boxes? Click to expand... That rule is specific to #4 and larger conductors. I don't think you'll have a communication cable that large. In any case, you still do need to plan for proper bend radius.