The code seems to imply that the Intersystem Bonding bridge should be near the service equipment or (or building disconnect at remote structures). Kind of sucks when the comm wires need to come in at the opposite side of the house. What kind of comm wires are installed (phone, CATV, ??)? If there is no connection to the comm utility, it may not be required to be grounded yet. The intersystem bonding bridge install sounds compliant, but not useful.
Note that external means not in the meter pan or service panel, but doesn't mean it has to be outside the house. Mine is inside the garage, next to the main panel. They don't want the DISH guy having to open the panel to connect his ground.
I would agree that the proper solution is to install another bridge near where the comm lines are going to enter the building and run a long #6 back to the service. Just not sure the code mandates it. The onus will be on the comm installer when they show up to connect to the utility or dish/antenna.