Not required by NEC or NFPA 780 as long as it is not supporting electrical devices or enclosures in which case I believe bonding is a requirement.
250.4 General Requirements for Grounding and Bonding.
(A) Grounded Systems.
(4) Bonding of Electrically Conductive Materials and
Other Equipment. Normally non–current-carrying electrically
conductive materials that are likely to become energized
shall be connected together and to the electrical supply
source in a manner that establishes an effective groundfault
current path.
(B) Ungrounded Systems.
(3) Bonding of Electrically Conductive Materials and
Other Equipment. Electrically conductive materials that
are likely to become energized shall be connected together
and to the supply system grounded equipment in a manner
that creates a low-impedance path for ground-fault current
that is capable of carrying the maximum fault current likely
to be imposed on it.
Is grounding required for a community college baseball field fence?
On the other hand, if freestanding light poles for the field are anywhere near the fence, even if not attached to it, a ground fault coupled with an inadequate EGC could well energize the fence through the earth....
I conclude that there is no general requirement to bond a fence unless it is likely to become energized, whatever that means. I think there is a requirement for pools and fountains and what not to bond nearby metal fences, but no such general requirement.
The long winded way of agreeing with you.
What do you mean by “grounding”? If you mean connection of a green or bare “equipment grounding conductor,” then I would ask what light bulb, light switch, scoreboard controller, or other electrical component would be installed onto the fence. They I would say bond the EGC from the circuit that feeds that component to the external metal parts of the component (you have to do that anyway), and also bond the component to the fence. The mounting bracket might be enough to do this job. But if there are no electrical components mounted on the fence, then this step has no meaning (and is not possible anyway).Is grounding required for a community college baseball field fence?
I was thinking similar, it can be bonded whether intentionally or not to a metal lighting pole, but if the lighting pole should become energized all it is likely to do for less then 300 volts to ground is to just energize the fence.On the other hand, if freestanding light poles for the field are anywhere near the fence, even if not attached to it, a ground fault coupled with an inadequate EGC could well energize the fence through the earth.
There have been a couple of threads with detailed reports of similar problems, in some cases with injuries.
As long as the lighting circuit is known to be OK, this is not a likely problem.
Sent from my XT1585 using Tapatalk
If within 5 feet of the inside walls of the pool, same for most any other conductive object near a pool.I conclude that there is no general requirement to bond a fence unless it is likely to become energized, whatever that means. I think there is a requirement for pools and fountains and what not to bond nearby metal fences, but no such general requirement.
The long winded way of agreeing with you.