K8MHZ
Senior Member
- Occupation
- Electrician
EC friend of mine did a service upgrade and put 3 2/0's in an outside run of 1 1/4" PVC. He said he looked it up in the book, and it was allowed.
Inspector pointed out that the table the EC was referring to was for compact conductors, not everyday conductors. He didn't make the EC change anything, but pointed out the section of the tables the EC should be referring to and just to not do it again. (We have cool inspectors here. They have common sense and everything.)
So, I took a look at a piece of the conductor the EC was using. It sure looked like the strands were pressed out of shape and most of them weren't perfectly round. It was obvious they had been 'compacted', but according to the inspector they were not 'compact conductors.'
If a conductor is 'compact', is that info on the conductor's insulation somewhere? If not, how does one determine if a conductor is compact or not?
Inspector pointed out that the table the EC was referring to was for compact conductors, not everyday conductors. He didn't make the EC change anything, but pointed out the section of the tables the EC should be referring to and just to not do it again. (We have cool inspectors here. They have common sense and everything.)
So, I took a look at a piece of the conductor the EC was using. It sure looked like the strands were pressed out of shape and most of them weren't perfectly round. It was obvious they had been 'compacted', but according to the inspector they were not 'compact conductors.'
If a conductor is 'compact', is that info on the conductor's insulation somewhere? If not, how does one determine if a conductor is compact or not?