Can someone advise what the closest delay curve is for a Carling G-series circuit breaker (hydraulic-magnetic) as compared to an industry standard K-curve for a thermal-magnetic breaker?
It would seem "Long" Curve 26. Typical TCCs for standard breakers have an instantaneous that is ~10x rated current. The short time / delay is not typically the same (Curve 26 is more slurred) as shown, but it is as close as it comes.
This is a typical 60-70A QO breaker https://download.schneider-electric...59.606325885.1691243079-1846500861.1676670757