I doubt the homeowner is going to want some rigged up way to get the power out there. Obviously, if he has a run that is 530' away, then he has a pretty large yard, and I imagine a large house and large wallet to go with it.
Things to remember, the large wire at 120V is probably not going to fit on the terminations, and additional splicing will be required. At 120V I think your asking for trouble.
Use three - 2pole breakers out of the panel and feed three 2-pole switches at Owner desired location (even though only two need to be switched, it makes it cleaner to have switches on all three). Run two 3/4" or even 1" conduits (conduits cheap after trench is dug) out to the 150' j-box location from the switches. Out of the J-box take the 240V SWD circuit out to each location. At each location set a 2KVA single phase, 240V primary - 120V secondary outdoor encapsulated transformer. You can even use the transformer taps to help keep the 240V circuit wire size down to a minimum out of the panel.
Looks like you could use #10AWG on the 530ft run, and #12 on the 400 and 410ft run. Using the taps on the transformer you might even be able to use #12AWG on all three circuits.
The smaller size conductor is certainly going to offset the cost of oversized wire, larger conduit, larger j-boxes, etc.