tryinghard
Senior Member
- Location
- California
Scenario: normal utility power also includes a kirk key transfer for a vehicle type portable generator to be plugged in when needed and the circuits include the following.
Service disconnect 100A breaker, #2s to subpanel main 100A breaker, and a periodic generator with 3ph 100A breaker (OCPD) connected to #6 SO cord, 50A cap & plug, #6s to subpanel with 45A backfed breaker kirk keyed with 100A main. I am not questioning the kirk key arrangement with lower main but do question the #6 cord, cap & recept, and #6 feeder from the generator’s 100A apparently using the downstream 45A protection – is this scenario compliant?
Service disconnect 100A breaker, #2s to subpanel main 100A breaker, and a periodic generator with 3ph 100A breaker (OCPD) connected to #6 SO cord, 50A cap & plug, #6s to subpanel with 45A backfed breaker kirk keyed with 100A main. I am not questioning the kirk key arrangement with lower main but do question the #6 cord, cap & recept, and #6 feeder from the generator’s 100A apparently using the downstream 45A protection – is this scenario compliant?