Compression coupling used between GRC and LFMC conduits

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
We have a 3/4 rigid metal conduit connected to 90 degree elbow, connected to a metal compression type coupling which connects to a 2 foot long LFMC and then attaches to electrical cabinet - the installation is indoors (not roof top)
Does the compression-type coupling interrupt the fault path? Or is the EGC within the circuit conductors sufficient?


Sent from my iPhone using Tapatalk
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
How is the compression coupling connected to the LFMC? Is there a rigid coupling on the end of the 90° elbow? I've never seen a direct RMC to LFMC fitting.
 

kwired

Electron manager
Location
NE Nebraska
How is the compression coupling connected to the LFMC? Is there a rigid coupling on the end of the 90° elbow? I've never seen a direct RMC to LFMC fitting.
I think I've seen them but not in a compression type, the RMC side was female pipe thread. I know I've seen FPT to EMT compression couplings
 
Top