Compression fittings for rigid conduit

Status
Not open for further replies.
There are compression fittings listed for wet location but the standard compression fittings cannot be used in wet areas.
 
If not so listed then no they cannot be used.

Welcome to the Forum. :)
I don't think threaded rigid couplings are listed for that use. Threaded rigid couplings leak a lot more than the old EMT compression couplings that we can no longer use in wet locations. Conduits in wet locations are required to be "arranged to drain". I don't see a real world issue if the couplings leak.
 
We use to use standard emt compression couplings outside because we were unaware that there was a product listed as rain-tite.
 
Would you consider rain tight/concrete tight to be the same as wet location rated? If so American fittings has plenty of options through PLATT https://www.platt.com/platt-electri...Fittings-Corp/NT2761/product.aspx?zpid=823924
I believe RAIN TIGHT is as wet location rated as your going to get with conduit fittings.

Cut sheet for both couplings and connectors --> http://amftgs.com/techlibrary/Rigid Conduit Couplings and Connectors Product Cut Sheets Online.pdf

Interesting issue - never considered this. I found these: Raintight SSR series by Eaton.

http://www.cooperindustries.com/con...sr_seriessetscrewrigidimcconduitfittings.html

Here are a few selections from the description:


only appear to be made for sizes 1/2 thru 2" :(
See post #9. :blink:

American Fittings fittings (just had to get that in there :D) contradict Eaton/Cooper's claim about the only line. Perhaps they mean the only line of their making. Just can't trust advertising anymore... even though it's not like we ever really could... just feels better to say it. ;)
 