A contractor has asked if he can use a compression fitting on existing RMC in a submerged-turbine-pump sump above an underground gasoline tank.
He is concerned about having to move the level of the pump's head and that the conduit will not match the new location.
I have recommended a explosion proof listed flex conduit since there are no compression fittings listed for this location.
Do you have any other suggestions?
(Translation: the contractor does not know how to thread conduit underground in a pit over a gas tank. He wants an easy way to change the location of the conduit to the pump.)