How would you size the feeder to two air compressor packages if this the only information provided on the manufactures label.
221HP, 165KW, 460volt 3PH.
The documents that came with the compressors list parallel runs of 3/0 as supply conductors and parallel 200 amp fuses (6 ea.).
When I requested more info from the manufacture, such as the minimum supply circuit conductor ampacity and the maximum ampere rating of the short circuit/ground fault device (430.7(D) (1) or what is the calculated FLC for the package, the emailed reply was:
Parallel 250MCM
6 200 amp fuse or 3 325 amp fuse class K5