Computer Room AC Unit

Status
Not open for further replies.

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
Reading the electrical data of the mechanical schedule. The FLA is 62.9 amps. DOes the disconnect need to be sized at 115% or 125% of FLA? Thanks.
 
Really doesn't matter as either number would be a 100 amp disconnect. The exact OCP would depend in the factory specs.
 
I can't say I blame you as I was curious also......
440.12 (1) Ampere Rating. The ampere rating shall be at least 115 percent of the nameplate rated-load current or branchcircuit selection current, whichever is great
but your FLA vs branch circuit selection current vs rated load current has a,ways been confusing to me so I just awaited nameplate data :)
 