Reading the electrical data of the mechanical schedule. The FLA is 62.9 amps. DOes the disconnect need to be sized at 115% or 125% of FLA? Thanks.
Funny I was going to say that in my post but still wanted to know which it was.Really doesn't matter as either number would be a 100 amp disconnect. The exact OCP would depend in the factory specs.
Not less than 115% of the sum of the rated load current per 440.12(B)(2), AND it must comply with the Horsepower rating per 440.12(B)(1).Funny I was going to say that in my post but still wanted to know which it was.