Re: Computer Room Cabling
GMGERRY, here is a list of highlights I use on data centers. Not sure if it is applicable in your situation.
1. Raised floor installed and used as plenum for HVAC supply air.
2. AC, plumbing, fire sensors, signal reference grid (SRG) installed under raised floor.
3. 2 or 3 tier 18? cable racks installed centered over equipment line-ups at 8?-6?, 9?-6?, & 10?-6?, supported from ceiling if possible or from stanchion pole and/or equipment racks otherwise. The cable racks are used to carry the all the signal cables and DC power, and DC grounds.
4. Lights installed centered over walk aisles in between equipment line-ups.
5. Sprinklers system installed as high as possible above all other systems.
6. PDU?s from UPS installed strategically in equipment line-up to keep dedicated branch circuits short so voltage drop does not exceed 3%. No IG outlets. PDU feeder and branch circuits ran under raised floor in approved raceway.
7. Battery breaker bays installed same as PDU except distribution is overhead on cable racks.
Hope this helps, suggest you get a copy of IEEE Orange, BUFF, Emerald, and Green books. And since I was recently laid-off, I would love to help out.
Bob I have used the device you pictured. So far I have only had to design a 645 compliant system in two cities, King of Prussia and Philly. Otherwise I avoid it like the plague.
Dereck
[ April 04, 2003, 11:09 AM: Message edited by: dereckbc ]