Re: Computer Room Power Shut Down
(1) is for the disconnecting means. For the disconnecting means you would shut down both power and HVAC.
(2) covers the smoke detection activation of the fire/smoke dampers of HVAC units that serve other areas, not shut down the unit (or any power to IT equipment).
Below floor detectors shutting down the below-floor HVAC is covered under 645.5(D)(3) only.
No where else does it indicate to shutdown power only upon activation of a below floor smoke detector.