Con Edison incoming service

Status
Not open for further replies.

defishu

Member
Location
new york
Anyone can help me with this?

How do we request Con Edison for incoming service with a demand load of 13,000 amp building.? 4 @ 4000 amp or what? 3@ 4000 amp is a little bit too less.
 
Not sure how 12,000 amps will work for a 13,000 amp load. How was the 13,000 amps calculated?
 
This is how we do it

https://www.coned.com/en/small-medium-size-businesses/building-project-center

Fill out the web forms


They will tell you if it is 480/277 or 120/208V

Then you will be told if it is one service or two or whatever.

Most of the time I ask for thousands of amps of service from ConEd, and I get one 4000A service entrance because they know that the Article 220 calculations are way too conservative. Then I take in one service entrance and break it into multiple 4000A service disconnects.
 