B buck Member Location California Apr 25, 2005 #1 Code states that you must bond around concentric/ eccentric knockout when not listed for grounding. Do panels, boxes, etc have information printed on them when they are in fact listed for grounding?
Code states that you must bond around concentric/ eccentric knockout when not listed for grounding. Do panels, boxes, etc have information printed on them when they are in fact listed for grounding?
B benaround Senior Member Location Arizona Apr 25, 2005 #2 Re: concentric/ eccentric knockouts I know that disconnects do. frank
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Apr 25, 2005 #3 Re: concentric/ eccentric knockouts I think that this requirement is only for bonding over 250 volts. Look at 250.97. [ April 25, 2005, 11:29 PM: Message edited by: infinity ]
Re: concentric/ eccentric knockouts I think that this requirement is only for bonding over 250 volts. Look at 250.97. [ April 25, 2005, 11:29 PM: Message edited by: infinity ]