Re: Concentric K.O.'s
Nathan, with the info you provide it is not a yes or no answer.
2002 NEC 250.97 requires bonding on circuits over 250 volts to ground, but there are exceptions to this.
It would be better if you read them yourself to see where your particular installation fits in, or provide more info.
You also could look at 250.118(7) which has a 6' maximum total length for using the flex as the grounding conductor.
It sounds like you ran a separate equipment grounding conductor, so in my opinion 250.118 does not apply.
I believe if you run an equipment grounding conductor and the voltage to ground is less than 250 volts you do not need bonding bushings for the flex that could be as long as you want.
Above 250 volts to ground you will need bonding bushings, unless your installation fits the exceptions.