DansProfElec
Member
- Location
- Huntington beach, CA
I was given a correction by the city inspector to install grounding bushings on 2 EMT screw connectors because we ran our 3/4" EMT through the 1" concentric knock outs of the subpanel (only the 3/4 knockout was removed). When I asked the inspector why we needed grounding bushings if there was a ground wire run in both EMT conduits, The inspector said the call is for seismic.
This is a 200 Amp subpanel in a commercial suite in California. Both 3/4" EMT's have #12 ground wires, running 2 20 Amp, 120 V circuits. All the EMT was secured to the concrete wall within 3 inches of the subpanel using strut.
Do you still have to install grounding bushings when using the concentric knockouts if you run a ground wire? If so what's the point of running a ground wire and bonding to all the ground screws in the j-boxes?
Can anyone site the code that says this.
Thanks,
Dan
This is a 200 Amp subpanel in a commercial suite in California. Both 3/4" EMT's have #12 ground wires, running 2 20 Amp, 120 V circuits. All the EMT was secured to the concrete wall within 3 inches of the subpanel using strut.
Do you still have to install grounding bushings when using the concentric knockouts if you run a ground wire? If so what's the point of running a ground wire and bonding to all the ground screws in the j-boxes?
Can anyone site the code that says this.
Thanks,
Dan