A raceway falls under 250.190(A). It is all one contiguous system. Ground cables are only required where 250.190(A) is broken. This section applies to every voltage. For instance in residential voltage the conduit is bonded but if for instance the conduit is PVC or the cable is NM-B, then the ground has to be landed at every metallic enclosure.
As to demonstrating compliance a conduit does have a lower specific resistance than copper or aluminum. However this is outweighed by the vastly larger cross sectional area. The raceway impedance is always lower than conduit fill rules allow. Having a separate ground would be required when using nonmetallic raceways or when trays are not bonded. In metallic raceways that are bonded, the EGC that is present is a supplemental ground. For instance hospital Code requires two separate ground paths so the raceway and an EGC are required. Jumpers are dictated by 250.190(C)(3) subject to the minimum in C(1).