I have an installation that I question involving metal junction boxes being installed above an eventual drop ceiling, with some that are currently secured to cantilevers which we don't typically approve.
I'm not certain if this is the only NEC reference, but based on how I interpret 314.23(B) regarding structural mounting, I don't believe that the current installation has the box properly supported using this installation. Since its not supported directly off the structural member, I would at a minimum expect a continuous metal support between beams to secure the box(es). Refer to the attached photo.
The installation includes EMT conduit, but 358.30 doesn't exclude installation of boxes in between structural members; only that they're securely fastened following the required intervals. The structural members are currently designed at a center to center spacing of just under 7 ft. I've referenced 2014 NEC Handbook related to this inquiry.
Would appreciate input on this interpretation.

I'm not certain if this is the only NEC reference, but based on how I interpret 314.23(B) regarding structural mounting, I don't believe that the current installation has the box properly supported using this installation. Since its not supported directly off the structural member, I would at a minimum expect a continuous metal support between beams to secure the box(es). Refer to the attached photo.
The installation includes EMT conduit, but 358.30 doesn't exclude installation of boxes in between structural members; only that they're securely fastened following the required intervals. The structural members are currently designed at a center to center spacing of just under 7 ft. I've referenced 2014 NEC Handbook related to this inquiry.
Would appreciate input on this interpretation.