Concession trailer

Status
Not open for further replies.
Depending on how one interprets the new gfci requirement for the receptacle your plugging your concession stand into - - -probably yes.hope your trailer has been properly wired as a 4 wire set-up with the ground isolated from the neutral.
 
Just finished inspection corrections on aconcession trailer.
Inspector wanted GFCI protection for all counter top plugs, & water pumps for wash basin/sink.
Did not require GFCI protection for top-level, ladder accessible plugs, controlling 120v lights & 120v roof Air Conditioner.

Replacing all Half-Switch/Plugs with GFCI devices was impractical. Was easier to re-wire junctions for separate neutrals to allow 1P GFCI breaker, then put GFCI stickers on the devices.

Snowie.com franchise dealer sold trailer with in-use 120v GFCI bolted to Homeline 4 / 8ckt, with both phase-legs shunted together.

Dealer specified 10-12kw for generator running all loads. That's 83 Amps going thru 120v GFCI feeding the fuse box.

Had to rewire everything for a NEMA 14-50 pigtail, and avoid cross wiring explosions using 240v Pedestal / Generator power.
 
It maybe high-time to add an article to NEC to address internal wiring of concession trailers kinda like the internal wiring of RV section.
 