Looking for comments on this-- taken from here E&S Grounding Solutions-- has a lot of code info. The article I am quoting can be downloaded but you have to sign up... http://www.esgroundingsolutions.com/downloads/electrical-grounding-tips-article/
I read this the other day and it made me think of the episodes that I have heard about with ufer's blowing out the concrete
However I have not heard of this before
I read this the other day and it made me think of the episodes that I have heard about with ufer's blowing out the concrete
Concrete
Many of the ground enhancement products contain concrete (often mixed with coke breeze), which is
typically installed around a copper conductor or ground rod. The primary purpose of this is to increase the
surface area and contact between the copper and the earth. The chief issue with concrete is that it has a
very poor current (amperage) handling ability. The water that is naturally found in concrete will quickly turn
into steam under fault conditions, cracking the concrete and thus making the electrode virtually useless. As
the electrode will be buried, you may never know that the electrode has been compromised.
However I have not heard of this before
Using a Water Pipe as
a Grounding Electrode
Everyone does it, but does a water pipe provide effective grounding? Unfortunately, the answer is almost
always a qualifi ed “No”. It is important to understand the difference between the terms bonded and
electrode when speaking about electrical grounding. A ”bonded” object is when an electrician makes an
intentional metallic connection to ensure that there is no difference in potential, but is NOT intending that
object to be used as a path to earth for electrical faults. An “electrode” IS an object that is intentionally
connected and designed to conduct electrical faults to earth (and typically buried).
Water pipes provide a poor path to earth for electricity as the utility company typically coats the pipes
with tar to prevent corrosion, installs electrically isolative barriers, or uses non-metallic pipes. This is why
the National Electric Code requires that an additional grounding electrode be installed along with the
connection to water pipe. It is better to think of water pipe as a required metal object that must be bonded
to the ground system, rather than thinking of it as an electrode for the ground system.