Condition 2 — Exposed live parts on one side of the working space and grounded parts on the other side of the working space. Concrete, brick, or tile walls shall be considered as grounded.
In this link, Zog posted some great info.
Dry concrete above grade 1-5 M ohms,
Dry concrete on grade 0.2-1 M ohms,
Wet concrete on grade 1-5 k ohms.
Of course resistance means nothing without an area / cross-section. In these examples I assume that the area is about equal to the contact area of an average boot sole.
Concrete is such a good conductor, it is the only acceptable ground electrode method the military will allow in bomb storage vaults and aircraft hangers.
Herbert G. Ufer invented what is known as A Ufer Ground during WWII. Today the NEC accepts a variant of the Ufer ground we call concrete encased ground electrode.
I have designed built quite a few of them in data centers and telephone switching offices, and in most cases the impedance is so low (less than 1 ohm) it cannot be accurately measured.
Thanks to everyone for replying. The reason I asked is that i took and ohm meter to concrete at work (inside in a dry area) and it would not register on the 200 ohm scale. It makes sense that the concrete closer to the earth and in direct contact with the earth will have a much higher moisture content and therefore, more conductive.
In this link, Zog posted some great info.
Dry concrete above grade 1-5 M ohms,
Dry concrete on grade 0.2-1 M ohms,
Wet concrete on grade 1-5 k ohms.
Of course resistance means nothing without an area / cross-section. In these examples I assume that the area is about equal to the contact area of an average boot sole.
If you have a panel in a room with the concrete on grade, take volt meter. Put one prod on the concrete floor, and the other prod on the bus of the panel. You should read very close to the actual reading of voltage at the panel.
Concrete that is in contact with the earth is a very good conductor.