Curious if anyone has ever installed conduits that had to be concrete encased. How do they encase the 5kv conduits? Build a form around them? How does that work with the trapeze? J
 

Attachments

  • Capture.jpg
    Capture.jpg
    18.3 KB · Views: 17

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Build a form and pour in the concrete. We usually hang the conduit with standard rod and strut then the iron worker builds the steel support around it to support the weight of the concrete.

20080209_78.jpg
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
So those painted black racks are yours supporting the conduits or for the concrete? Doesnt the concrete need supporting?

They appear to be for the concrete. Your drawing calls for supports every 4 feet. It also shows the "box" is re-barred to the hilt, really turning it into a beam. You didn't say if the conduits were plastic or steel, but if the latter that's just additional support for the concrete.
 

macmikeman

Senior Member
When I have to encase conduit runs underground in concrete, I put saddles not only holding the pipe up off the bottom of the trench, but also ones going to the left side, some going to the right side of the trench. I'll throw. those in between the ones every 4 foot that hold the conduit off of the bottom of the trench. Then if it is a wide trench, I'll usually build a form around the conduit as well so that if it ever has to be located and dug up there is not some 24" wide concrete mess to deal with when the thing has to get jackhammered. (if ever) This technique makes sure that the concrete will evenly flow under and around and then on top of the pipe, unlike just laying conduit in the trench and then pouring concrete on top of it. It all depends on whether there is going to be an inspector, and what type of job it is-non government but going under a driveway or under a street, or City, State, or Federal job. If nobody is looking, and its just a code requirement due to a driveway or something- just lay the conduit on the bottom and pour some concrete on top. A guy with a shovel comes along and he is gonna hit that concrete and slow himself down pretty quick. Same for a backhoe. Most guys won't just keep on digging it up, they find out what the hell it is and then deal with it somehow.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
So those painted black racks are yours supporting the conduits or for the concrete? Doesnt the concrete need supporting?

Yes, the black racks are connected to the building steel and are there to support the weight of the concrete, they're installed by the iron workers. The conduit was installed first using standard threaded rod then the steel framework was built around it. Next the forms were added and the concrete poured.

Your installation had a similar detail with the exception of how the steel framework is supported with a poured concrete deck above.
 

Ingenieur

Senior Member
Location
Earth
Build a form and pour in the concrete. We usually hang the conduit with standard rod and strut then the iron worker builds the steel support around it to support the weight of the concrete.

View attachment 20089

your method makes sense
in the op detail they cast a w beam thru the duct bank
this leaves the bottom unsupported
also the side connections look insufficient imo, the 2 x 2 3/4" bolts support 4'
the 4' with concrete, cnd/cond, rebar and w beam might weigh 2800 lbs or 700/bolt in shear

also the hanger saddle is welded, no flex or give like a bolted or pinned connection
the whole 4' assy section is hanging by a 2 x 2 x 6" x 1/4" weld bead
all in shear or 24" x 1/4" x 1/4" x 1/2 = 3/4 cu in od steel
1/2 on the side, 1/2 on the bottom
each tranferring 100% or 2800 lb
 
Last edited:

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
One would think that a sheet metal form could have been used that could have been left in place. sheet metal is cheap. labor to remove forms is not.

If by "sheet metal" you mean 3 gauge steel, sure. If you mean HVAC-type sheet metal, not a chance.
 