designer82
Senior Member
- Location
- Boston
Sec. 300.50(A)(3) says that "other nonshielded cables... shall be encased in 3in. concrete"
Most of the time, I see the utility primary (and even secondary) U/G power service cables installed in concrete encased ductbank. It doesn't seem the NEC requires this, the only section I've found is the one shown above.
Are utility primary cables unshielded most of the time? In that case it would make sense.
thank you
Most of the time, I see the utility primary (and even secondary) U/G power service cables installed in concrete encased ductbank. It doesn't seem the NEC requires this, the only section I've found is the one shown above.
Are utility primary cables unshielded most of the time? In that case it would make sense.
thank you