I've read dozens of threads on the forum regarding this topic, but I've not seen an answer to the following specific question:
Assume I'm bonding all grounding electrodes together present at my building, to include building structural steel, cold water piping, concrete-encased electrode, and (2) ground rods per NEC 250.50. Per Table 250.66, my GEC should be #1/0 based on service entrance conductor size.
Does my concrete-encased electrode also need to be #1/0, or can it be #4 AWG as described in 250.52(A)(3) and just be bonded to the rest of the grounding electrode system with a #1/0?