tecelec1st
New member
- Location
- denver, colorado
does the 2014 require concrete encased electrode?
And that is generally interpreted to mean that if there is qualifying rebar the CEE exists even if you forgot to connect a GEC to it before pouring the concrete. :slaphead:You do not have to make one but if one exists you must use it.
You do not have to make one but if one exists you must use it.
Yes, but...
For existing, would not that be determined whether by the ability to access without damage given the exception?
Exception: Concrete-encased electrodes of existing build-
ings or structures shall not be required to be part of the
grounding electrode system where the steel reinforcing bars
or rods are not accessible for use without disturbing the
concrete
I would not consider a foundation recently poured as part of the same project I am working on to be existing.
But if the building was complete and certified for occupancy before I started I should be OK.
If it gets poured before you get there, it's existing.
Ask Dennis. NC has an amendment that says so.
Many places only require a footing inspection and when the EC or electrical inspector shows up, too late. Sad but true.
The footing inspector also looks for the concrete encased electrode here. He will not permit the pour unless there is some provision for the concrete encased electrode. We also permit the concrete contractor to connect a #4 copper to the rebar and stub it out for the future use of the EC. Often the EC has not even been selected at the time the footing is poured so this solves the issue for us.If it gets poured before you get there, it's existing.
Ask Dennis. NC has an amendment that says so.
Many places only require a footing inspection and when the EC or electrical inspector shows up, too late. Sad but true.
If it gets poured before you get there, it's existing.
Ask Dennis. NC has an amendment that says so.
AMENDMENT 250.50Amend NEC 2014, page 117:
250.50 Grounding Electrode System. Allgrounding electrodes as described in250.52(A)(1) through (A)(7) that are available ateach building or structure served shall be bondedtogether to form the grounding electrode system.Where none of these grounding electrodes exist,one or more of the grounding electrodesspecified in 250.52(A)(4) through (A)(8) shallbe installed and used.
But in one way this goes farther than the NEC and requires all CEEs to be used when there is more than one while the NEC only requires you to connect to one.That's true, it's basically the same wording as the 2002 NEC.
Roger
And Dennis hates that amendment... I generally install a ufer but occasionally my builders screw up. If they made it a rule then they wouldn't forget it but once.
The footing inspector also looks for the concrete encased electrode here. He will not permit the pour unless there is some provision for the concrete encased electrode. We also permit the concrete contractor to connect a #4 copper to the rebar and stub it out for the future use of the EC. Often the EC has not even been selected at the time the footing is poured so this solves the issue for us.
That's true, it's basically the same wording as the 2002 NEC.
Roger
Here is the current wordingBut in one way this goes farther than the NEC and requires all CEEs to be used when there is more than one while the NEC only requires you to connect to one.
All grounding electrodes as described in 250.52(A)(1) through
(A)(7) that are present at each building or structure served shall
be bonded together to form the grounding electrode system.
Where none of these grounding electrodes exist , one or more of
the grounding electrodes specified in
250.52(A)(4) through (A)(8)
shall be installed and used.
The footing inspector also looks for the concrete encased electrode here. He will not permit the pour unless there is some provision for the concrete encased electrode. We also permit the concrete contractor to connect a #4 copper to the rebar and stub it out for the future use of the EC. Often the EC has not even been selected at the time the footing is poured so this solves the issue for us.
If I was the building owner that would not be acceptable to me.In Washington, if there is a new building and a connection is not made to reinforcing steel, then you go in and make the connection.
See photo
If I was the building owner that would not be acceptable to me.
The footing inspector also looks for the concrete encased electrode here. He will not permit the pour unless there is some provision for the concrete encased electrode. We also permit the concrete contractor to connect a #4 copper to the rebar and stub it out for the future use of the EC. Often the EC has not even been selected at the time the footing is poured so this solves the issue for us.
Devil's advocate... if a building inspector inspected the footings and confirmed there was reinforcement that is one thing, if there is no such inspection is it right for an EI to demand breaking up a footing to look for reinforcement that may or may not be there?