210.52(A)(3) Concrete-Encased Electrode. A concrete-encased elec-
trode shall consist of at least 6.0 m (20 ft) of either (1) or (2):
(1) One or more bare or zinc galvanized or other electri-
cally conductive coated steel reinforcing bars or rods of
not less than 13 mm ( 1 ⁄ 2 in.) in diameter, installed in
one continuous 6.0 m (20 ft) length, or if in multiple
pieces connected together by the usual steel tie wires,
exothermic welding, welding, or other effective means
to create a 6.0 m (20 ft) or greater length; or
(2) Bare copper conductor not smaller than 4 AWG
Metallic components shall be encased by at least 50 mm
(2 in.) of concrete and shall be located horizontally within that
portion of a concrete foundation or footing that is in direct
contact with the earth or within vertical foundations or struc-
tural components or members that are in direct contact with
the earth. If multiple concrete-encased electrodes are present
at a building or structure, it shall be permissible to bond only
one into the grounding electrode system.