weressl
Esteemed Member
I think I understand the intent of 250.50 Grounding Electrode System to be that all underground metallic objects should be bonded together to minimize and avoid the flow of objectionable current between them by equalizing the potential difference between the different areas and to gain higher grounding resistance.
I personally believe that the Ufer type grounding of utilizing the concrete rebars was what seemed to be a good idea and it gained popularity by avoiding the installation of external additional grounding systems. What I think is lacking is sufficient research and study of the actual installation where it can be proven that the resultant corrosion - due to DC component of any grounding current and the lime content of the concrete as an electrolyte - does not jeopardize the structural integrity that the rebar serves in the first place.
When Epoxy coated rebars are used for additional corrosion resistance then then I presume taht they are not required to be bonded to the grounding system.
The latest addition of the Code seem to ignore or contradict the original purpose. " Where multiple concrete-encased electrodes are present at a building or structure, it shall be permissible to bond only one into the grounding electrode system." This preceeded by the " Reinforcing bars shall be permitted to be bonded together by the usual steel tie wires or other effective means".
Questions 1: Do they required to be or permitted to be bonded together?
Question 2: Are they permitted to be bonded toegther to form the length of the electrode that is defined under this section?
Question 3: What is the value of effective bonding? How do you measure it?
Question 4: If the original intent is to bond all underground metallic objects - less the exceptions - together why ony one rebar is required to be bonded and not all?
I personally believe that the Ufer type grounding of utilizing the concrete rebars was what seemed to be a good idea and it gained popularity by avoiding the installation of external additional grounding systems. What I think is lacking is sufficient research and study of the actual installation where it can be proven that the resultant corrosion - due to DC component of any grounding current and the lime content of the concrete as an electrolyte - does not jeopardize the structural integrity that the rebar serves in the first place.
When Epoxy coated rebars are used for additional corrosion resistance then then I presume taht they are not required to be bonded to the grounding system.
The latest addition of the Code seem to ignore or contradict the original purpose. " Where multiple concrete-encased electrodes are present at a building or structure, it shall be permissible to bond only one into the grounding electrode system." This preceeded by the " Reinforcing bars shall be permitted to be bonded together by the usual steel tie wires or other effective means".
Questions 1: Do they required to be or permitted to be bonded together?
Question 2: Are they permitted to be bonded toegther to form the length of the electrode that is defined under this section?
Question 3: What is the value of effective bonding? How do you measure it?
Question 4: If the original intent is to bond all underground metallic objects - less the exceptions - together why ony one rebar is required to be bonded and not all?