engy said:IMO Yes if a floating slab. (not slab between footings/walls?)I see no depth requirement in NEC.
The handbook notes make it quite clear this is acceptable (we all know how much weight that carries?)![]()
![]()
Makes me wonder how well a floating slab performs as a CEE sitting on four feet of frost.:-? (Only applies to those of us up here in the hinterland, ya know.)
raider1 said:What do you mean by "floating slab"?
I have both the 2005 and the 2008 NEC handbook and neither one appears to show a slab as a CEE.
I agree with Trevor, a concrete slab is not a footing or a foundation.
Chris
engy said:Floating slab has no footing/foundation that extends down below the frostline.
Typically the edges are beefed-up a bit and contain rebar.
I believe it wouldn't take much to call something a foundation.
2008 Exhibit 250.22 & 250.23
dnem said:Since you brought up Exhibit 250.23, where does the NEC say you have to install a "nonmetallic protective sleeve" where the electrode conductor exits the concrete ?
raider1 said:What you describe is called a monolithic slab in my area and the thicked edges that contain rebar are footings.
Chris
steve66 said:So does this building need a CCE or not? Steve
steve66 said:Then I have one more question that the Architect needs to answer - is there a moisture barrier between the concrete and the ground??
Steve
steve66 said:250.64(B) (2005) ??
Steve
A/A Fuel GTX said:Chris....What if the monolithic slab had no rebar? Could I still lay a #4 in the bottom of the thickend edge and have an adequate CEE or would I have to place the #4 suspended within the concrete to meet the 2" reference in 250.52(A) (3)?
engy said:I recall from a previous thread, that the consensus was "who cares", because the poly would not act as an insulator anyway. (and the code does not seem to care, or at least account for...)
earshavewalls said:...If you must break up concrete to get to it, you don't have to use it.
raider1 said:I must have missed that thread, it has always been my contention that the footing or foundation need to be in direct contact with the earth and that a vapor barrier would cause and issue as it would separate the footing or foundation from the earth.
Chris
earshavewalls said:Here in LALA land (California), most use the entire reinforcement system, which is tied together, to act as one grounding electrode/ufer. The code just says that you CAN use this method, and that if it is available, you must use it. If you must break up concrete to get to it, you don't have to use it.