Concrete-Encased Electrode.

Status
Not open for further replies.

tcook99

Member
Location
Florida
How can I get an official interpellation of 250.66(B) as the sole means for grounding for a service over 3/0. From NFPA. This is a 400 amp service sized per 310.15(B)(6). New construction with no other means available per 250.50.
Single family dwelling. I need something official from NFPA.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Good luck with an official NFPA document. If the CEE is the only electrode present than that's the only one required. #4 CU is also the largest conductor required to a CEE. 250.66(B).
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
infinity said:
Good luck with an official NFPA document. If the CEE is the only electrode present than that's the only one required. #4 CU is also the largest conductor required to a CEE. 250.66(B).

I agree with the others, a CEE can be a sole electrode and it only needs to be connected by a #4 conductor.

Roger
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I would add one other thing, that if the footing didn't contain 1/2" or larger rebar no CEE would be required. Then you could just use 2 ground rods.
 