T titletownu.s.a Member May 17, 2005 #1 Is there a mechanical lug rated for direct encasement in concrete or is cad weld the only option to ground to rebar?
Is there a mechanical lug rated for direct encasement in concrete or is cad weld the only option to ground to rebar?
ryan_618 Senior Member Location Salt Lake City, Utah May 17, 2005 #2 Re: Concrete encased electrode There are mechanical lugs for this application.
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician May 17, 2005 #3 Re: Concrete encased electrode Per UL any connector listed for direct burial is also suitable for use in concrete. Don
Re: Concrete encased electrode Per UL any connector listed for direct burial is also suitable for use in concrete. Don