I'd like to throw out some questions for discussion and opinions. There are three methods that I see in my area for providing a concrete-encased electrode. The two most common are:
1)A length of bare #4 copper, usually solid, but occasionally stranded is placed in the footing so that at least 20' runs parallel with the footing rebar. This is usually loosely draped around a rebar and is sometimes clamped to a rebar, sometimes not. The other end is long enough to come out the top of the foundation. Usually it is long enough to reach unspliced to the disconnect enclosure. In this approach, I believe the #4 copper wire is an NEC legal concrete-encased electrode and the contact with and/or clamping to the rebar is just added value.
2) a length of #4 copper conductor is clamped to the rebar in the footing and run out the top of the foundation. Often this conductor is long enough to run unspliced to the disconnect. In this approach there is no particular length of the #4 copper than runs along the length of the footing. In this approach, I believe the #4 copper is a GEC and the footing rebar is the NEC recognized concrete-encased electrode.
3) A third, less common method is to bend a 20' length of footing rebar so that one end comes out of the top of the foundation. The lower leg of the bent rebar is tied to the rest of the footing rebar with the usual wire ties.
My questions are:
1) Does anyone see anything about any of these approaches that would be a violation of the NEC?
2) Any opinions as to which method provides the best electrode over time? Does anyone have any data to support an opinion one way or another? I wonder about the effect of moisture and contact with concrete on the copper wire over time.
3) Is the green copper oxidization film a conductor or is it an insulator. If approach #1 above is used, will oxidization cause the electrode to become less effective over time?
1)A length of bare #4 copper, usually solid, but occasionally stranded is placed in the footing so that at least 20' runs parallel with the footing rebar. This is usually loosely draped around a rebar and is sometimes clamped to a rebar, sometimes not. The other end is long enough to come out the top of the foundation. Usually it is long enough to reach unspliced to the disconnect enclosure. In this approach, I believe the #4 copper wire is an NEC legal concrete-encased electrode and the contact with and/or clamping to the rebar is just added value.
2) a length of #4 copper conductor is clamped to the rebar in the footing and run out the top of the foundation. Often this conductor is long enough to run unspliced to the disconnect. In this approach there is no particular length of the #4 copper than runs along the length of the footing. In this approach, I believe the #4 copper is a GEC and the footing rebar is the NEC recognized concrete-encased electrode.
3) A third, less common method is to bend a 20' length of footing rebar so that one end comes out of the top of the foundation. The lower leg of the bent rebar is tied to the rest of the footing rebar with the usual wire ties.
My questions are:
1) Does anyone see anything about any of these approaches that would be a violation of the NEC?
2) Any opinions as to which method provides the best electrode over time? Does anyone have any data to support an opinion one way or another? I wonder about the effect of moisture and contact with concrete on the copper wire over time.
3) Is the green copper oxidization film a conductor or is it an insulator. If approach #1 above is used, will oxidization cause the electrode to become less effective over time?