mshields
Senior Member
- Location
- Boston, MA
I'm working on a high rise project where the service equipment (S&C gear plus two pad mounts) is located in a vault on the second floor of the building. We are running through the garage in a concrete encased primary feeder all inaccordance with the NEC. Some of this duct is supported by steel structural elements specifically installed to support the duct (the building itself is actually concrete). The architect is questioning whether or not these steel supports should be fire proofed with the spray on stuff. My response is as follows. I'd be interested in your insights - thanks
My response:
I don't see anything in National Grid's special provisions nor in their general requirements, requiring fire proofing of supports for the concrete encased primary lines in the building. It does nevertheless strike me as consistent with the rational behind requiring concrete encasement to begin with. This an NEC requirement by the way, not the utilities.
The reasoning is that whereas the rest of the building can be de-energized from the service disconnect switches within the building this primary leg cannot be.
You are therefore left with a scenario where the Fire Department does not have a means of de-energizing this one component within the building. It is therefore required that this feeder be made bullet proof or more to the point, fire proof to reduce the chances of it rupturing and electrocuting someone. If the support for the busduct is not fireproofed, then it stands to reason that neither is the duct itself.
I do not know of nor can I find a specific mention of this in the NEC. Still, I think it should be done.
My response:
I don't see anything in National Grid's special provisions nor in their general requirements, requiring fire proofing of supports for the concrete encased primary lines in the building. It does nevertheless strike me as consistent with the rational behind requiring concrete encasement to begin with. This an NEC requirement by the way, not the utilities.
The reasoning is that whereas the rest of the building can be de-energized from the service disconnect switches within the building this primary leg cannot be.
You are therefore left with a scenario where the Fire Department does not have a means of de-energizing this one component within the building. It is therefore required that this feeder be made bullet proof or more to the point, fire proof to reduce the chances of it rupturing and electrocuting someone. If the support for the busduct is not fireproofed, then it stands to reason that neither is the duct itself.
I do not know of nor can I find a specific mention of this in the NEC. Still, I think it should be done.